I guess this is mostly for other Cinemarkers because it's building-specific... but has anybody had this problem? Our building has been said to be the last of the "Tinseltown" design. It was built in 1996, just before they switched to the "stadium" design. In fact, they say our building was almost going to be stadium until they changed their minds at the last minute... Anyway, here's the problem:
Every morning when you go in to open up you find all the platters and the tops of the lamphouses covered with dust bunnies. It seems that when the air conditioning kicks-on in the morning the "surge" of air blows all the crap out of the ducts and out into the room. Of course, somebody had the bright idea to put all the vents right above the projectors! Sometimes it hapens during the day, too. Especially if it's hot outside and the AC cycles on and off a lot. (It only happens diring the summer when the AC runs -- Not when the burners run for heat.) I'm not entirely sure which duct it's comming from. It might be the ventillation ducts or it might be the air-return ("balancer") ducts. Of course, having dust bunnies attacking our film isn't a good thing. Especially since we've worked so hard in the last year to clean up our presentation. It feels like one step forward and two steps back, sometimes! Any ideas?
| IP: Logged
|
|
|
|
|
|
Bruce McGee
Phenomenal Film Handler
Posts: 1776
From: Asheville, NC USA... Nowhere in Particular.
Registered: Aug 1999
|
posted 06-05-2000 06:46 AM
Hey Randy! This is a subject that I KNOW.Has your theater got electronic air cleaners instead of regular air filters installed in the HVAC system? When they are turned off, the minute particles that collect on the charged surfaces are released and in some systems the particles fall into the ducts. The next time the blower starts.... If no EAC system, how often are the air filters changed? I've seen many commercial set-ups that have had the same filters in them for months, and are clogged. Also, who supplies the filters? Your theatre or the service co? If you can see through the new filters, just think how much crud gets thru them. I look for filters that are thick. They cost more, but are worth it. I have an EAC on my home HVAC system that had problems blowing white dust all over everything. I installed the filters just past the EAC and stopped all dust. All I have to do is vacuum the filter surface every couple of months and they last forever, well, a year or more anyway. Honeywell Air Systems RULE! (I do not work for Honeywell, but I DID work in heating and cooling for 7 years!)
| IP: Logged
|
|
John Pytlak
Film God
Posts: 9987
From: Rochester, NY 14650-1922
Registered: Jan 2000
|
posted 06-05-2000 08:10 AM
Really efficient disposable air filters (e.g. 3M "Filtrete") are readily available and relatively low in cost. Use the "HEPA" pleated media filters rather than the cheap spun fiberglass filters. The "HEPA" filters trap dust particles down to the sub-micron size. Good filtration of the incoming air will not only keep the film cleaner, but also electronic (disk drives) and optical components (reflectors, port glass). If necessary, you could make frames to hold standard-size filters in front of each air duct. Don't forget to change the filters when they load up with dust.------------------ John P. Pytlak, Senior Technical Specialist Worldwide Technical Services, Entertainment Imaging Eastman Kodak Company Research Labs, Building 69, Room 7419 Rochester, New York, 14650-1922 USA Tel: 716-477-5325 Fax: 716-722-7243 E-Mail: john.pytlak@kodak.com
| IP: Logged
|
|
John Walsh
Film God
Posts: 2490
From: Connecticut, USA, Earth, Milky Way
Registered: Oct 1999
|
posted 06-05-2000 09:34 AM
Another cheap thing that might help is some kind of baffle to keep air from directly blowing on the platters; something to direct the airflow out to the middle of the room. The filter on the vents is a better idea, though.I wish I had a nickle for evey stupid architect mistake, like vents directly over the film, or (my fav) return ducts behind the screen so dirt get drawn into the holes. In "clean-rooms" for IC wafer maufacturing, they find that (after filtering the incomming air) the next problem is dust from people's clothing. The doors to clean-rooms have an "air-wash," where a big blower blasts you (while in a sort of air-lock) before you go in. If an even "cleaner" room is needed, that's when they make you wear the "bunny-suits." I actually wanted to make a simple version of a clean room at a 10-plex theater we were building a few years ago to use as a prototype to see if it was worth designing in all of our new theaters. I had read about clean-room design and wanted to take some of those ideas, (using a certain kind of paint and ceiling tiles, separate closed filtered intake for the lamps, etc.) but (no surprise) no one in management was interested.
| IP: Logged
|
|
John Pytlak
Film God
Posts: 9987
From: Rochester, NY 14650-1922
Registered: Jan 2000
|
posted 06-05-2000 10:07 AM
"Cleanrooms" magazine has much information on contamination control: http://www.cleanrooms.com Cleanroom technology is essential to the manufacture of microelectronic components and photographic film. Kodak's film and microelectronic manufacturing areas have air-jet/vacuum "people washers" and require "bunny suits" (cleanroom coveralls for shoes, clothing, hair and beards) to enter. Such extreme measures are usually not needed for projection rooms. Easily cleaned worksurfaces, good air filtration and good housekeeping are usually all that is needed to maintain clean film images. On-line film cleaners are recommended to remove any dirt picked up during projection. The most important "rule" is not to let the film or leader come in contact with a dirty surface. Operators who say "it's only leader" or "I don't have time to wipe off the rewind bench" are usually the ones with the dirty prints. ------------------ John P. Pytlak, Senior Technical Specialist Worldwide Technical Services, Entertainment Imaging Eastman Kodak Company Research Labs, Building 69, Room 7419 Rochester, New York, 14650-1922 USA Tel: 716-477-5325 Fax: 716-722-7243 E-Mail: john.pytlak@kodak.com
| IP: Logged
|
|
|
Bruce McGee
Phenomenal Film Handler
Posts: 1776
From: Asheville, NC USA... Nowhere in Particular.
Registered: Aug 1999
|
posted 06-06-2000 06:59 PM
Maybe they are not changing the filters often enough? The Condenser is the part that is outside on the A/C system. The Evaporator is inside the duct work, unless this is a package unit on the roof. Most commercial systems that I installed used a low or medium speed on the motor for heating, and high for cooling. Maybe the system is running when they change filters? If so, they are stupid. All that does is get the evaporator coil dirty, reducing efficency, and spread junk thru the duct system, which is what you are probably seeing on the equipment. Spun filters are OK, but cheap filters are no bargain! I am using Precisionaire PSF filters in all the systems that I service. I've never had a dust problem with them. The company that I worked at for all those years has used them for 15 years. They come in all standard sizes.You might check, if possible, to see if all the filters are installed correctly. There is an arrow pointing which way the air is supposed to flow through them. It does make a difference! Trane stuff is good. GE made the compressor that they used to hawk as being indestructable (Remember the WeathertronŽ heat-pumps of the early '80's? Same compressor, and they are still running.) Most heat-pumps last around 10-12 years before the compressor dies. GE no longer owns the compressor design, or has leased it to Trane and they now build it themselves. I have installed several roof-top package systems over the years, but no theatre jobs. I always hoped that I could do that just once! It would be a good idea to install filter material over the supply ducts in the booth. They can be changed every month or so when they get dirty. Unfortunately, the duct system is probably caked with grey dust by now. Changing to better filters will fix the problem, but, all the crud that is in the ductwork will have to work its way out. Hope I have not bored you to death. Bruce
| IP: Logged
|
|
|
Jason Burroughs
Jedi Master Film Handler
Posts: 654
From: Allen, TX
Registered: Jun 99
|
posted 06-07-2000 01:40 PM
Cinemark has been using the Norvar/Trane package for some time, and in my experience they both work pretty well. Bruce was right about the compressors, I've never seen one of them having to be replaced, and they get quite a workout here in Texas, Weakest point I've seen in the Tranes (particularly the older models) is the condensor coils, they have some weak spots in the line and leaks will eventually develop allowing the Freon to leak out. Compare that to the Aaon's and Lennox units that I've worked with they're top notch. I think the key points have already been touched on, make sure the filters are replaced on a regular basis and done properly, seal the port windows as much as possible, you'll notice the port windows get DIRTIER on the outside than the inside due to the enviroment of people comming and going, draperies, chairs capret etc... One thing you might suggest, since you're theatre is a few years old is to have the ducts in the booth professionally cleaned.
| IP: Logged
|
|
John Pytlak
Film God
Posts: 9987
From: Rochester, NY 14650-1922
Registered: Jan 2000
|
posted 06-07-2000 02:04 PM
Jason:I agree with your suggestion to have the ducts professionally cleaned if they have a buildup of debris. Even new ductwork often has alot of construction "crud" left in them. Once the ducts are cleaned, be meticulous in changing the filters properly and frequently. Another worthwhile idea to improve booth cleanliness is to have a central vacuum cleaning system installed, exhausted to the outside. Using a shop vac, broom, or dry mop just tends to stir up the dirt, so it lands elsewhere. Wet-mopping works well if you're on a budget. The guy who thought of using blowers to clean the auditorium should be made to clean out each perforation in the screen with a toothpick, one hole at a time! The dust raised by the blowers also finds it's way onto the port glass, and even into the booth. I recall another thread mentioned watching the placement of the HVAC ducts so they don't suck or blow dirty air through the perforated screen. ------------------ John P. Pytlak, Senior Technical Specialist Worldwide Technical Services, Entertainment Imaging Eastman Kodak Company Research Labs, Building 69, Room 7419 Rochester, New York, 14650-1922 USA Tel: 716-477-5325 Fax: 716-722-7243 E-Mail: john.pytlak@kodak.com
| IP: Logged
|
|
|
All times are Central (GMT -6:00)
|
|
Powered by Infopop Corporation
UBB.classicTM
6.3.1.2
The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion