Topic: Bad Lamps and Power Readings
|
|
|
|
|
Stephen Furley
Film God
Posts: 3059
From: Coulsdon, Croydon, England
Registered: May 2002
|
posted 02-20-2003 05:38 AM
Tim wrote:
quote: 30 amp breaker with 33amps running through it can get pretty hot, and even discolor the breaker.
This doesn't sound right. A breaker passing 10% over its rated current shouldn't be getting hot, and most need more than a 10% overload to trip. If a breaker is getting as hot as you say it is then there is something wrong, either it is passing much more current than you think it is, in which case it should have tripped, or the contacts are poor, dirty, pitted, etc., and there is a high resistance there. Another possibility is bad connections between the breaker and its cables. Apart from any other problems you may have, I think you need to overhaul, or replace this breaker, it sounds like a safety hazard in its present condition.
| IP: Logged
|
|
|
|
|
All times are Central (GMT -6:00)
|
|
Powered by Infopop Corporation
UBB.classicTM
6.3.1.2
The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion