I have been trying to solve a heat problem with a "Super Highlight" lamphouse. This lamphouse has survived many a bulb explosion and now the reflector looks like minced meat. Factors contributing to the problem include an employee (fired) who did not tighten the electrical connections when installing a new bulb. I spoke with an employee at Ballantyne to get some helpful information. I mentioned to him that we were running CXL50SC's in the lamphouse and he remarked that the lamphouse was only designed to cool a bulb of 4000W max. I proposed that I was thinking of adding additional cooling to the lamphouse by cutting a hole in the front, mounting an external squirell cage fan and blasting air towards the bulb. The person I spoke with said this should help, but I noticed while perusing posts here at film-tech that overcooling the bulb can be bad. Any suggestions??

So far I have suggested replacing the reflector, installing a new original cooling fan, and installing an extra cooling fan.

Thanks,

ERIC

 |  IP: Logged

Michael Schaffer
"Where is the
Boardwalk Hotel?"

Posts: 4143
From: Boston, MA
Registered: Apr 2002


 - posted 05-24-2005 09:20 PM      Profile for Michael Schaffer   Author's Homepage   Email Michael Schaffer   Send New Private Message       Edit/Delete Post 
And check if the top exhaust meets specifications, if it exhausts enough air from the lamphouse. The airflow is measured in cfm (cubic feet per minute) and normally specified in the lamphouse manual.

 |  IP: Logged

Mark Gulbrandsen
Resident Trollmaster

Posts: 16657
From: Music City
Registered: Jun 99


 - posted 05-24-2005 09:49 PM      Profile for Mark Gulbrandsen   Email Mark Gulbrandsen   Send New Private Message       Edit/Delete Post 
My God! Don't go by what it says in the manual. The manual spec. is beyond stupid, something that Stong needs to get smart about! LAst one I read sped's about 400 to 600 cfm, barely enough.....
For a 2kw to 3kw lamp you need 900+ cfm, for a 4kw or larger about 1500+ cfm. If on doubt about what exactly you have call in an HVAC guy and have it measured. Also be sure the present blower is not running in reverse, a common problem at least in this area.

Mark @ CLACO

Mark

 |  IP: Logged

Richard Hamilton
Phenomenal Film Handler

Posts: 1341
From: Evansville, Indiana
Registered: Jan 2000


 - posted 05-24-2005 10:00 PM      Profile for Richard Hamilton   Email Richard Hamilton   Send New Private Message       Edit/Delete Post 
Eric,
What size screen, Just curious why you are running a bigger lamp than designed for. Has this screen always been a problem? I would try a new reflector and make sure everything is aligned properly with the correct bulb first.

Rick

 |  IP: Logged

Monte L Fullmer
Film God

Posts: 8367
From: Nampa, Idaho, USA
Registered: Nov 2004


 - posted 05-25-2005 01:07 AM      Profile for Monte L Fullmer   Email Monte L Fullmer   Send New Private Message       Edit/Delete Post 
..might have to shove a booster fan in the stack plumbing to really get some draw out of that lamphouse..especially with 50K bulbs....That's a scorcher an a half!

 |  IP: Logged

Eric Robinson
Jedi Master Film Handler

Posts: 538
From: Santa Rosa, CA
Registered: Jan 2005


 - posted 05-25-2005 10:06 AM      Profile for Eric Robinson   Email Eric Robinson   Send New Private Message       Edit/Delete Post 
I had an HVAC tech measure all of our airflows. This particular projector measured 773 CFM with an 8 inch Duct. Sounds like I need to have it upgraded to 1500 CFM at a minimum?

I will have to measure the screen size, but it is very large and I would guess the throw at about 70 feet. It may be possible that a 4000 or 4500 watt bulb would work, but I'm guessing it might be a little dark.

Currently when projecting light on the screen with the lens removed there are black spots scattered around the screen on about 50% of the image, so I'm guessing that the reflector damage has decreased the light output by 50 to 60% or maybe more.

Also...forgot to mention that the fellow I talked to at Ballantyne said that measuring the bulb temperature with a probe near the front of the bulb where the glass and metal meet is the best way to determine a temperature problem. He stated that the bulb warranty for Christie specifies that the junction or bulb seal should not exceed 180 degrees Celcius during operation. I set up my meter to measure the temperature and all was well until I restruck the bulb while my meter was hooked up and turned on. I'm guessing the igniter pulse fried the circuitry in my meter because it would only read -1 on every range, scale, etc...

I thought it might be a good idea to install an electronic temperature guage in the lamphouse which would disable the lamp in the event of exceeding a specified threshold temperature.

Any comments about my idea to install an extra fan to blow directly on the bulb?

 |  IP: Logged

John Pytlak
Film God

Posts: 9987
From: Rochester, NY 14650-1922
Registered: Jan 2000


 - posted 05-25-2005 11:15 AM      Profile for John Pytlak   Author's Homepage   Email John Pytlak   Send New Private Message       Edit/Delete Post 
A good reflector and proper alignment will likely provide a significant improvement in light output. But even with a properly curved 70-foot gain screen, a 4K lamp will fall short of getting the 16 footlambert aim specified by standard SMPTE 196M. Running a larger lamp "hot" in a lamphouse that was not designed for it is not the best solution.

 |  IP: Logged

Monte L Fullmer
Film God

Posts: 8367
From: Nampa, Idaho, USA
Registered: Nov 2004


 - posted 05-25-2005 01:06 PM      Profile for Monte L Fullmer   Email Monte L Fullmer   Send New Private Message       Edit/Delete Post 
Might have to do a console changout. Christie "Reference" consoles can easily use 6k bulbs with no problem and these consoles have dual fans - one on top of the console to blow on the anode and the internal to blow on the cathode. This has a 20inch mirror and these units can put out excellent light when filling 35x66 ft screens at 95 feet.

With this, definitely a 1500cfm to pull tha heat out.

-monte

 |  IP: Logged

Randy Stankey
Film God

Posts: 6539
From: Erie, Pennsylvania
Registered: Jun 99


 - posted 05-25-2005 02:15 PM      Profile for Randy Stankey   Email Randy Stankey   Send New Private Message       Edit/Delete Post 
You need one of these: www.infrared-usa.com

An non-contact infrared thermometer is essential for testing xenon lamp temperature. The price of these things is so cheap, nowadays, that virtually anybody can get them.

I have never tried to measure the temp of my xenon. I wouldn't try it with the lamp burning. I'd run the thing for a while then shut it off for a minute before carefully opening the lamphouse and "zapping" the lamp. You won't get the exact temperature but you'll get a reading that will tell you if your lamp is burning in the "danger zone". Not only is it dangerous to open the lamphouse with the lamp burning but the IR that comes from the arc will throw the reading off. I doubt the temperature of the lamp will vary by more than a few degrees in 5 minutes.

I can tell you that my projector aperture gets as hot as 200 deg. F. when its running and the lamphouse itself gets up to about 130 deg.

If the film is 75 deg when it enters the projector it will be about 100 deg when it hits the lower sprocket in the projector. By the time it gets back to the platter it's at about 85.

This is with a little ol' 2000 Watt lamp inside a Xe-Lamp enclosure. I just can't imagine what temperature YOUR setup is hitting with a lamp THAT big! [Eek!]

 |  IP: Logged

John Hawkinson
Film God

Posts: 2273
From: Cambridge, MA, USA
Registered: Feb 2002


 - posted 05-25-2005 03:58 PM      Profile for John Hawkinson   Email John Hawkinson   Send New Private Message       Edit/Delete Post 
Umm, Randy, you can take a thermocouple probe from a multimeter and shove it into the duct above the stack fan and then you can take live measurement safely.

--jhawk

 |  IP: Logged

Rick Long Jr
Expert Film Handler

Posts: 211
From: Toronto, Canada
Registered: Jul 2000


 - posted 05-25-2005 06:52 PM      Profile for Rick Long Jr   Email Rick Long Jr   Send New Private Message       Edit/Delete Post 
I've added the same blower Strong uses on the Highlight 2's to the top of older Highlight/Super Highlight consoles to aid cooling with large bulbs. It helps, but these old consoles were basically an X-60 in a larger box, which had poor cooling anyway. The newer design with the enclosed box inside forces more air through the reflector hole.

 |  IP: Logged

Randy Stankey
Film God

Posts: 6539
From: Erie, Pennsylvania
Registered: Jun 99


 - posted 05-25-2005 09:10 PM      Profile for Randy Stankey   Email Randy Stankey   Send New Private Message       Edit/Delete Post 
I only mentioned the non-contact IR thermometer because Eric said that he already toasted a DMM trying to do it that way.

Besides being really handy the things are just plain fun to have around! [Smile]

 |  IP: Logged

Michael Schaffer
"Where is the
Boardwalk Hotel?"

Posts: 4143
From: Boston, MA
Registered: Apr 2002


 - posted 05-26-2005 06:32 PM      Profile for Michael Schaffer   Author's Homepage   Email Michael Schaffer   Send New Private Message       Edit/Delete Post 
Speaking of airflow meters, I am tired of borrowing it from our AC guys. What do you think of this one here?

 |  IP: Logged

Bevan Wright
Expert Film Handler

Posts: 176
From: Fountain Valley, CA, USA
Registered: Sep 2003


 - posted 05-26-2005 07:43 PM      Profile for Bevan Wright   Author's Homepage   Email Bevan Wright   Send New Private Message       Edit/Delete Post 
Try one of these - http://www.technika.com/navpage/a1.htm

 |  IP: Logged

John Walsh
Film God

Posts: 2490
From: Connecticut, USA, Earth, Milky Way
Registered: Oct 1999


 - posted 05-27-2005 07:19 AM      Profile for John Walsh   Email John Walsh   Send New Private Message       Edit/Delete Post 
I have an Extech 407114 which has worked well, but I'm thinking of getting an air flow meter with a probe, such as the 407117. To get an accurate reading with the traditional spinning vane type you usually must remove the vent pipe, position the vane inside, and close it up. That is, you need to hold the vane inline with the pipe while preventing air leaking around the pipe'e diameter, reducing the accuracy. This is awkward to do sometimes. With the probe type, you only need to make a small hole (easily plugged with a removable plastic plug) and insert the probe.

 |  IP: Logged



All times are Central (GMT -6:00)  
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.

© 1999-2020 Film-Tech Cinema Systems, LLC. All rights reserved.