Oscar Neundorfer
Master Film Handler
Posts: 275
From: Senoia, GA
Registered: May 2000
|
posted 11-20-2006 04:13 AM
Has this problem existed from the initial installation or has it recently started? You said it was "flickering intermittently throughout the day". Have you been able to correlate the flickering with any other event at the theatre such as large motor loads kicking on, like HVAC, for example?
The three dimmers ideally should all be on the same phase, and absolutely should not be sharing neutrals. Each should have a separate neutral running all the way back to the panel. Same goes for the lighting loads. In some cases where the 3 phase and neutral were brought to the console and distributed in the console, neutrals all the way back to the panel are not always easily done.
In any event make sure the neutrals are not daisy chained from one to the next, to the next, and then back to the neutral buss bar, whether the buss bar is in the console or back at the distribution panel.
I can't explain why the one with the fan flickers less. The only reason for the fan was that this model had a slightly higher inductance choke for less lamp singing efect, and would run slightly hotter. So the fan kept it cooler. Perhaps the higher choke inductance is making it slightly less susceptible to flickering effects which might be caused by wiring issues or other causes.
One other suggestion is to go through the system and make certain there are no loose connections on any of the wiring terminals either on the dimmers or at the distribution terminals. Over time, things tend to loosen up and can cause problems. Check hots, neutrals, and grounds. Also make sure each dimmer is securely grounded with a separate ground wire from the ground terminal back to the distribution ground buss. As usual, take the proper precautions and remove power at the breakers before doing this type of work.
SMART dimmers were known to be fairly problem free except for some issues with early models driving magnetic low voltage loads such as Tivoli lighting. This was usually manifest as breaker tripping at turn on, not flickering.
Hope something here helps.
Oscar
| IP: Logged
|
|
|
All times are Central (GMT -6:00)
|
|
Powered by Infopop Corporation
UBB.classicTM
6.3.1.2
The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion