Stephen Furley
Film God

Posts: 3059
From: Coulsdon, Croydon, England
Registered: May 2002


 - posted 03-25-2007 06:17 AM      Profile for Stephen Furley   Email Stephen Furley   Send New Private Message       Edit/Delete Post 
Strange problem yesterday evening. Kinoton lamphouses, Irem rectifiers.

Starting the adverts and trailers for the 6 O'clock show. Just as I opened the curtains the lamp went out; couldn't restrike it. Shut everything down and re-started, lamp won't light. Check the main three phase breaker for the rectifier; it's tripped. Reset the breaker and try again; as soon as the lamp strikes the breaker trips again. At this point the audience has been staring at a blank screen for the best part of a minute, so I abandon the adverts, reset the masking for scope and start the feature. After about five minutes I try to strike the lamp on the problem machine, and it's fine. Try again about 30 minutes later, still fine. Decide that the problem seems to have fixed itself, and go ahead with the changeover to that machine; no problems, and everything was fine with the next, and last, show.

No strange sounds, smells, sparks, smoke etc. from lamphouse or rectifier, but I'm a bit concerned that the breaker should have tripped twice; I've only ever had it happen once, and that was several years ago; I can't remember if it was the same rectifier.

Faulty breaker possibly? I can't see anything wrong with the equipment. The cinema is closed today; I'll e-mail the chief in the morning and let him know.

 |  IP: Logged

Louis Bornwasser
Film God

Posts: 4441
From: prospect ky usa
Registered: Mar 2005


 - posted 03-25-2007 04:29 PM      Profile for Louis Bornwasser   Author's Homepage   Email Louis Bornwasser   Send New Private Message       Edit/Delete Post 
In USA 3 phase breakers get worn and only 2 connections are made. Then when you strike, it is too much without the third. Is this possible? In any event, I would swap the breaker as a precaution especially if you use it everyday to cut off power when you leave. Louis

 |  IP: Logged

Michael Schaffer
"Where is the
Boardwalk Hotel?"

Posts: 4143
From: Boston, MA
Registered: Apr 2002


 - posted 03-25-2007 07:35 PM      Profile for Michael Schaffer   Author's Homepage   Email Michael Schaffer   Send New Private Message       Edit/Delete Post 
And, of course, trace and check all the connections visually and mechanically (meaning check for visible discoloration anywhere and loose connections).

Since you typically can't switch between manual and auto strike on the Kinoton lamphouses - at least not as far as I can remember, and it has been a few years since I have played with any of the older lamphouses which I think you have -, it is not easy to check if the tripping occurs when the rectifier is switched on or when the lamp strikes. One way to check that is to switch off the lamphouse with the switch on the back, open the rectifier and push and hold the contactor in firmly (there should be a little push button at the side) with an insulated screwdriver.

Obviously, this is a little [Eek!] dangerous [Eek!] when you don't know what you are doing, but I think you are a big boy and you do know what you are doing. Just a standard warning to remind people who read this not to do it unless they are sure they understand the risks.

You just wait for a few seconds and see if anything happens, next you flip the lamphouse switch to on and see what happens then. That should bring you a little more clarity.

If I remember incorrectly, it may also be that the contactor pulls in when you run the motor, even if the lamphouse is switched off. But I don't think so. In any case, you should close the big douser on the front, if you have it and/or run the motor anyway because it's not good if the lamp comes on when the front of the lamphouse is open and the machine is not running.

 |  IP: Logged

Demetris Thoupis
Phenomenal Film Handler

Posts: 1240
From: Aradippou, Larnaca, Cyprus
Registered: Apr 2001


 - posted 03-26-2007 01:54 AM      Profile for Demetris Thoupis   Email Demetris Thoupis   Send New Private Message       Edit/Delete Post 
What we call it in greek is "apolia", loss in connection or something like this in the electrical speech! It means that you either have some humidity build up in the breaker or the cables or the piping or the connections that make a small contact between each phase or a phase with a neutral of a phase with the earthing that causes the breaker to trip. Probably the humidity dried out after a while and that is why the breaker stood up! I don't know if I explained it correctly.

 |  IP: Logged



All times are Central (GMT -6:00)  
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.

© 1999-2020 Film-Tech Cinema Systems, LLC. All rights reserved.