Topic: CP650 rebooted mid-show for no particular reason, WTF?
|
|
|
|
|
|
|
|
|
|
|
|
|
|
Steve Guttag
We forgot the crackers Gromit!!!
Posts: 12814
From: Annapolis, MD
Registered: Dec 1999
|
posted 12-06-2008 11:46 AM
Most UPSs actually switch the power from line to battery in a power failure...this brings about a relay contact that can be either faulty or a contact not properly made.
In fact, I have a facility where the Crestron brain and a Media Matrix plugged into an APC rack mount UPS...after about 3 years of service, when there was a power failure at the facility, those two devices (Media Matrix and Crestron) clearly responded as if they were rebooted though the Media Matrix might not have booted up properly (note, the facility went on line in 2003 so that is the era of the equipment).
The A/V contractor in-charge of this equipment refused to believe it was the APC UPS since the batteries registered as good and they could unplug the APC and it performed properly. I countered with..."you have two otherwise unrelated devices having problems and the only commonality is the UPS that they both plug into." Note too, there are three other Crestron brains and one other Media Matrix on site, also plugged into APCs (different actual units) and they did not suffer the problem. It was way too much of a coincidence that the two devices plugged into this common box would be the subject of bizzar reboot problems.
So, on my insistance, and against the A/V contractor's recommendation, they plugged the Media Matrix and the Crestron into a mere Surge Suppressor/line conditioner (Tripplite LCR-2400)...zero problems with either box. The UPS was thrown in the trash and was replaced with a brand new unit and there have been zero problems since.
The better kind of UPS are the ones that generate their own sine-wave power and ALWAYS have the plugged in devices on UPS power. Think of the batteries as "buffers." They are always being filled while the unit is plugged in...if the power is lost, the batteries will then drain. However, the equipment that is plugged in is unaware of any power change. There is no transition time and the power is always clean.
Steve
| IP: Logged
|
|
|
|
All times are Central (GMT -6:00)
|
This topic comprises 2 pages: 1 2
|
Powered by Infopop Corporation
UBB.classicTM
6.3.1.2
The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion