Topic: Projection Booth requirements?
|
|
Tony Bandiera Jr
Film God
Posts: 3067
From: Moreland Idaho
Registered: Apr 2004
|
posted 10-28-2009 11:59 PM
James:
You're pretty close on the power requirements. Here's what I spec as a minimum:
1- 20amp 120v for projector motor, each machine; 1- 20 amp 120v for dowsers, etc. one circuit for both machines; 1- 30 amp, three phase for each rectifier; 1 - 20 amp outlet circuit will suffice for rewind bench, etc. Place the outlets where needed. Only your booth layout will know where.
For sound racks, a MINIMUM of 4 -20 amp, 120v circuits, one circuit for the processor, booth monitor and other gear ahead of the amplifiers, and circuits for the amplifiers that I group as left and right, center and surround, and subs.
Ventilation WILL be your biggest pain in the ass to deal with, as anyone who has never dealt with projection gear will argue endlessly over why it is needed and in the CFM needed. With that said:
A MINIMUM of 450 CFM, measured at a 6" dia. stack located just above the lamphouse. 600 CFM would be best, but don't go over that as too much cooling can cause problems as well.
**STAND YOUR GROUND ON THE VENT REQUIREMENTS, DON'T LET ANYONE SHORTCHANGE IT FOR ANY REASON or you WILL pay for it later in increased bulb and reflector failures!!
Also make sure that the lamp exhaust blower is under the EXCLUSIVE control of the projectionist, don't allow it to be tied into any building energy management systems!! UC Irvine has learned this expensive lesson the hard way with damage to a $3,000 glass reflector in a Kinoton lamphouse.
A 2k lamp will in most areas be required by building codes to be vented outdoors. You might get away with venting into the building, but I wouldn't try it.
Booth lighting should be a mix of general lighting (fluorscent lamps) for setup and maintenance, and dimmable downlights for use when the films are running. A wall-mounted track light on a dimmer to act as a projector worklight would be a good idea too.
Watch for my upcoming pics of my current install to be posted to the picture gallery here on F-T.
| IP: Logged
|
|
Frank Angel
Film God
Posts: 5305
From: Brooklyn NY USA
Registered: Dec 1999
|
posted 10-30-2009 02:15 AM
Tony hit all the right spots. And about the ventilation control - It's something even the electrical designers don't take into account. We had a very bad situation here on that same note -- the booth vent fans were controlled by nice big press on (green) - press off (red) industrial-type button switches with a big 7w green pilot light on the booth wall, but no one knew that down 6 stories below in the bowels of the building was a maintenance room with electrical panels and, yes, you guessed it, identical switches that paralleled the ones up in the booth.
I had been running that booth for maybe 10 years and never was there any indication that there was a clone of the switches elsewhere until one night when I was running a late show, I started to feel light-headed and even a little nauseous. I began to have a funny taste in my mouth and the room seemed to be hazing up. Some fool from the college maintenance dept was wandering around that electrical room and saw buttons with lights lit up. And he turned them off....hey they were shiney things, what more reason did he need? The college you see closes on the weekends and it's hard to get it thru their heads that the weekends are when we work.
Anyway, I realized in time that the exhaust had been turned off. In a carbon arc booth, it is even more dangerous than xenon given the toxic crap, including carbon monoxide, that a carbon arc lamphouse spews out if it's not seriously exhaused. So as Tony points out, yell and make lots of noise now in the planning stage, else you will have to be fixing that mistake later down the line and probably on your own.
Me, I just went down to the electrical room in the basement, opened up the switch box and disconnected and tied off the wires. Put a big sign on it too: "This switch as been disabled for critical safety reasons. Reconnect it under pain of....well, have you seen THE TEXAS CHAINSAW MASACRE?"
| IP: Logged
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
All times are Central (GMT -6:00)
|
This topic comprises 2 pages: 1 2
|
Powered by Infopop Corporation
UBB.classicTM
6.3.1.2
The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion