Our electrical panel has a stinger leg on one of the three phases. Im installing a Barco DP100 and am wondering if the orientation of the stinger leg is relevant.

 |  IP: Logged

Mark Gulbrandsen
Resident Trollmaster

Posts: 16657
From: Music City
Registered: Jun 99


 - posted 10-21-2011 07:23 AM      Profile for Mark Gulbrandsen   Email Mark Gulbrandsen   Send New Private Message       Edit/Delete Post 
Watch your maximum AC input with the BARCO. HIgh AC voltage can cause premature or outright failure of the power supplies or the rectifier components. I believe in the DP-100 manual it says absolute maximum is 230 volts ac. Your stinger (high leg) is going to be too high! An inexpensive buck boost transformer can be used to drop that leg down to a managable level. Better yet a 3 phase transformer or three seperate transformers to convert the booth AC into Y from your present Delta configuration would be the best route to go. You's end up with 208 three phase just like any modern new building has and that wold create much love between the AC voltage and the projector.

 |  IP: Logged

Robert Minichino
Master Film Handler

Posts: 350
From: Haskell, NJ, USA
Registered: Dec 2005


 - posted 10-21-2011 08:23 AM      Profile for Robert Minichino   Author's Homepage   Email Robert Minichino   Send New Private Message       Edit/Delete Post 
I'm not familiar with the specifics of the Barco, but if it requires a neutral (a 3-phase Wye connection), you need a transformer. If it doesn't require a neutral, and uses a Delta connection, all three of your legs are 240V, and it will work fine without a transformer. The one leg is only "high" with respect to the neutral (which comes from the center tap of one of the transformers supplying your building), and if the equipment doesn't use a neutral, this doesn't matter.

 |  IP: Logged

Louis Bornwasser
Film God

Posts: 4441
From: prospect ky usa
Registered: Mar 2005


 - posted 10-21-2011 08:46 AM      Profile for Louis Bornwasser   Author's Homepage   Email Louis Bornwasser   Send New Private Message       Edit/Delete Post 
Robert is right. Further, even if it is "neutral referenced" it may be possible to orient the phases so that the one (if present) that isn't neutral referenced is on the "stinger."

Sometimes popscorn machines and old Xetron consoles are like this. Louis

 |  IP: Logged

Eric Robinson
Jedi Master Film Handler

Posts: 538
From: Santa Rosa, CA
Registered: Jan 2005


 - posted 10-21-2011 05:14 PM      Profile for Eric Robinson   Email Eric Robinson   Send New Private Message       Edit/Delete Post 
The supply to the Barco does not include a neutral. Only L1, L2, L3, and Ground. I noticed that the Barco lamphouse itself draws power from a line jack connection on the control panel area. There is a line cord which plugs in there and it leads into the compartment where the 3 phase is hooked up. I was thinking I might need to trace it to make sure that this is not connected to the stinger leg. One thing I'm confused about though is that if the Barco projector head has this connection...I would assume it to be 120VAC. If so, how could it get 120VAC from a 3 phase connection that has no Neutral reference?

 |  IP: Logged

Phil Ranucci
Expert Film Handler

Posts: 236
From: Carpinteria,CA, United States
Registered: May 2006


 - posted 10-21-2011 06:37 PM      Profile for Phil Ranucci   Email Phil Ranucci   Send New Private Message       Edit/Delete Post 
I believe that the electronics (card cage) run on 208VAC. If you look inside the left panel at the top you'll see where they wired the electronics. Barco uses an IEC plug that is wired across 2 phases, so you need to make sure you get 208 across them. It could be OK on 240VAC, but I'm used to 3 phase without any complications.

 |  IP: Logged

Dave Macaulay
Film God

Posts: 2321
From: Toronto, Canada
Registered: Apr 2001


 - posted 10-21-2011 07:46 PM      Profile for Dave Macaulay   Email Dave Macaulay   Send New Private Message       Edit/Delete Post 
The IEC cable jumper is for connecting a UPS for the electronics. It is, indeed, 208/240 VAC.

 |  IP: Logged

Pete Naples
Phenomenal Film Handler

Posts: 1565
From: Dunfermline, Scotland
Registered: Feb 2001


 - posted 10-22-2011 03:50 AM      Profile for Pete Naples   Email Pete Naples   Send New Private Message       Edit/Delete Post 
Excuse my ignorance, what is a 'stinger' leg?

I've never ehard of that here in the UK, well Scotland.

 |  IP: Logged

Dave Macaulay
Film God

Posts: 2321
From: Toronto, Canada
Registered: Apr 2001


 - posted 10-22-2011 08:28 AM      Profile for Dave Macaulay   Email Dave Macaulay   Send New Private Message       Edit/Delete Post 
accidental duplicate

 |  IP: Logged

Dave Macaulay
Film God

Posts: 2321
From: Toronto, Canada
Registered: Apr 2001


 - posted 10-22-2011 08:28 AM      Profile for Dave Macaulay   Email Dave Macaulay   Send New Private Message       Edit/Delete Post 
This is an oddball 3-phase distribution wiring, it's not installed now as a rule so you won't see it very often but old industrial area still have it.
It is basically 240V delta with one of the distribution transformer's coils centre tapped to give two 120V legs on that phase. This "dog leg" or "stinger" leg is generally grounded to give 120V power to the facility. The voltage from the stinger to the third phase is not used for anything. This system has no neutral, voltage between any two phases is 240V.
This was popular in the beginning of industrial power distribution. The only 120V load in a factory back then was lighting. The problem is load imbalance, all 120V load is on one phase. Nowadays we have so much 120V stuff the imbalance is serious, so this wiring scheme was abandoned.
To get wye out of this and supply a neutral, you need a transformer.
3-phase loads usually have jumpers or another way to accept delta power, the dogleg won't cause any difficulty unless your machine wants a neutral.
240V is fine for a Barco, European power is normally 240V not 208. 208V is an artifact of our 117V to neutral Wye 3-phase. Single phase power here is 117/234. I don't know what happened to 120/240.

 |  IP: Logged

Monte L Fullmer
Film God

Posts: 8367
From: Nampa, Idaho, USA
Registered: Nov 2004


 - posted 10-22-2011 09:45 PM      Profile for Monte L Fullmer   Email Monte L Fullmer   Send New Private Message       Edit/Delete Post 
Side question then: where does 277v comes from? I notice that a lot of new large building uses 277 for their lights and for the simple reason of adding more load per breaker and not increasing current demand.

 |  IP: Logged

Pete Naples
Phenomenal Film Handler

Posts: 1565
From: Dunfermline, Scotland
Registered: Feb 2001


 - posted 10-23-2011 05:47 AM      Profile for Pete Naples   Email Pete Naples   Send New Private Message       Edit/Delete Post 
Thanks Dave [thumbsup]

 |  IP: Logged

Dave Macaulay
Film God

Posts: 2321
From: Toronto, Canada
Registered: Apr 2001


 - posted 10-23-2011 07:37 AM      Profile for Dave Macaulay   Email Dave Macaulay   Send New Private Message       Edit/Delete Post 
277v is the single leg to neutral voltage from 277/480V 3 phase wye distribution. 277/480v is an alternative to the 347/600v system, both used for commercial and industrial installations. This one is preferred in projects with a lot of motors, motors that can be used on this voltage are readily available and cheaper than the 575V ones needed for the 347/600v system. Most commercial buildings in Toronto have 347/600 and use 347V lighting - again so you can have more fixtures on a 15A breaker.

 |  IP: Logged

Christos Mitsakis
Expert Film Handler

Posts: 242
From: Ag.Paraskevi, ATHENS, GREECE
Registered: Sep 1999


 - posted 10-23-2011 08:24 AM      Profile for Christos Mitsakis   Email Christos Mitsakis   Send New Private Message       Edit/Delete Post 
For Pete:

High leg delta

 |  IP: Logged

Eric Robinson
Jedi Master Film Handler

Posts: 538
From: Santa Rosa, CA
Registered: Jan 2005


 - posted 11-04-2011 09:25 PM      Profile for Eric Robinson   Email Eric Robinson   Send New Private Message       Edit/Delete Post 
Thanks everyone. Indeed the card cage seems to be happy with 240VAC. Everything is working fine.

 |  IP: Logged



All times are Central (GMT -6:00)  
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.

© 1999-2020 Film-Tech Cinema Systems, LLC. All rights reserved.