Author Topic: False Fire Alarm Incident
Chad M Calpito
Master Film Handler

Posts: 435
From: San Diego, CA
Registered: Apr 2006


 - posted 06-13-2006 11:32 AM      Profile for Chad M Calpito   Author's Homepage   Email Chad M Calpito   Send New Private Message       Edit/Delete Post 
Last night, while getting ready to head to Projector #10 to shut it down for the night, the Fire Alarm System was activated by some stupid kids. This caused both Projectors #1 & #10 to shut down automatically since those are wired into the Alarm System. But, my remaining projectors that were running (#3, #6 & #9), I had to shut off manually.

Anyway, the Fire Department Came along with police. Luckily, there wasn't a fire, but, the customers were inconvenienced. Of course, Re-Admission Tickets were handed out to the remaining customers. After about 40-50 minutes of trying to deactivate the Fire Alarm System, I re-started #3, #6 & #9. But, the alarm system was still going and I could not do a regular re-start of #1 & #10, so I just did a manual start using the CNA-100 Automation.

Anyway, to the point, who else has experienced a False Fire Alarm incident, whether it be Floor Staff, Management, etc? I ask because this is my 3rd time going through this (twice at Regal Cinemas & once here at Pacific Theatres Grossmont Center 10).

Luckily, the False Fire Alarm incident happened during the last part of our Late Set, since five auditoriums were completely empty after the last shows.

 |  IP: Logged

John T. Hendrickson, Jr
Jedi Master Film Handler

Posts: 889
From: Freehold, NJ, USA
Registered: Apr 2001


 - posted 06-13-2006 06:50 PM      Profile for John T. Hendrickson, Jr   Email John T. Hendrickson, Jr   Send New Private Message       Edit/Delete Post 
We've had this happen several times. When the alarm goes off, for whatever reason (hand pull, heat sensor, smoke sensor) all of our projectors shut down. I have 10 screens with CNA 100 automation, and three with Kelmar, and the shutdown is instantaneous.

I'm curious to understand why three of your projectors did not shut down. If that problem persists, you should get a tech in to check it out.

In our situation, the Fire Marshall has to reset the alarm system, and you can't restart until that is done by him. If anyone else were to attempt to reset the alarm, it would land them in big trouble.

 |  IP: Logged

David Buckley
Jedi Master Film Handler

Posts: 525
From: Oxford, N. Canterbury, New Zealand
Registered: Aug 2004


 - posted 06-13-2006 11:34 PM      Profile for David Buckley   Author's Homepage   Email David Buckley   Send New Private Message       Edit/Delete Post 
There are ways to help the false alarm problem.

In the UK its common (but not universal) practice at live theatres to have the fire alarm system operate a few red lights in specific areas, so that the management and staff have a chance to evaluate if there really is a fire and if there isn't then to cancel the alarm. If not cancelled the system goes into full alarm after 30 secs or a minute usually. If two or more sensors trigger then a full alarm is immediately triggered.

If you have a lot of false alarm problems and the local fire people are amenable, you could do the same thing. In the UK if you called the fire brigade out for a falsie there used to be heinous charges for wasting their time, but I dont know if that is still the case.

 |  IP: Logged

Robert Burtcher
Expert Film Handler

Posts: 194
From: Oklahoma City, Oklahoma
Registered: Jun 2005


 - posted 06-13-2006 11:53 PM      Profile for Robert Burtcher   Email Robert Burtcher   Send New Private Message       Edit/Delete Post 
quote: John T. Hendrickson, Jr
I'm curious to understand why three of your projectors did not shut down.
quote: Chad M Calpito
This caused both Projectors #1 & #10 to shut down automatically since those are wired into the Alarm System. But, my remaining projectors that were running (#3, #6 & #9), I had to shut off manually.
I read this as saying that #1 & #10 are wired into the alarm system, but the others are not.

 |  IP: Logged

Chad M Calpito
Master Film Handler

Posts: 435
From: San Diego, CA
Registered: Apr 2006


 - posted 06-13-2006 11:56 PM      Profile for Chad M Calpito   Author's Homepage   Email Chad M Calpito   Send New Private Message       Edit/Delete Post 
The reason why three of my projectors didn't shut down instantaneously is because they were not hooked up to the Fire Alarm System. The only ones that are hooked up are projectors #1 & #10. Those are the Simplex Highlight II's with CNA-100 Automation. The 10 screen complex I work at started out as a 3 screen, then grew to an 8-plex, then in 1998, grew to a 10-plex. Anyway, I agree that all projectors should be hooked up to the alarm system. Plus, you brought up a good point to discuss this with the technician. Thanks for the tip, John.

Anyway, you are correct, Robert, that #2-#9 aren't wired into the system.

 |  IP: Logged

Jason Winn
Expert Film Handler

Posts: 131
From: Mesquite, TX, USA
Registered: Jan 2006


 - posted 06-14-2006 12:29 AM      Profile for Jason Winn   Email Jason Winn   Send New Private Message       Edit/Delete Post 
This happened once at the theatre I used to work at. I think it was a Friday night. It was probably around 10 or 11 PM. The fire alarm went off. All the projectors shut off right away. It was a false alarm though. A manager got on the PA system to inform everyone that it was just a false alarm. Then, we had to restart each projector one at a time. I don't understand why kids think it's so funny to pull the fire alarm. They're freakin' stupid!

 |  IP: Logged

Chad M Calpito
Master Film Handler

Posts: 435
From: San Diego, CA
Registered: Apr 2006


 - posted 06-14-2006 12:44 AM      Profile for Chad M Calpito   Author's Homepage   Email Chad M Calpito   Send New Private Message       Edit/Delete Post 
I agree with you, Jason. I did forget to mention that we have these stupid, idiot kids on our security cameras and the Grossmont Center Mall got the make & model of their car as well as the car's license plate number.

When this incident took place, I got all pissed off. [Mad]

 |  IP: Logged

Christopher Crouch
Expert Film Handler

Posts: 128
From: Holywood, ca, usa
Registered: May 2006


 - posted 06-14-2006 01:04 AM      Profile for Christopher Crouch   Email Christopher Crouch       Edit/Delete Post 
I've been through that quite a few times. In particular, I worked at a theatre that had a pull station next to a rear hallway exit door, adjascent to a payphone. Talk about enticing would-be trouble makers. We were having near weekly false alarms for a while. Then, we installed one of those alarm hoods over the pull station. In order to pull the lever, the person had to remove the plastic hood, which sounded a localized alarm of it's own. The high pitched squeel of that alarm hood managed to scare off most false pull attempts.

 |  IP: Logged

Jack Ondracek
Film God

Posts: 2348
From: Port Orchard, WA, USA
Registered: Oct 2002


 - posted 06-14-2006 03:26 AM      Profile for Jack Ondracek   Author's Homepage   Email Jack Ondracek   Send New Private Message       Edit/Delete Post 
quote: John T. Hendrickson, Jr
In our situation, the Fire Marshall has to reset the alarm system, and you can't restart until that is done by him. If anyone else were to attempt to reset the alarm, it would land them in big trouble.

Amazing, how cities can have very different approaches to this.

When the fire marshal inspected my indoor theatre, he specifically authorized a system whereby all public pull stations would show at an annunciator station in the concessions area. A manager would then investigate the situation and, if necessary, activate the alarm that would shut down the booth and call the fire department. There was a delay involved which would automatically set off the alarm after a certain time if the manager did not reset the system or set it off himself.

Smoke and heat detectors automatically fired off the full alarm. However, the Fire Marshal recognized the disruption that a public pull station could have, and allowed for the modified system.

 |  IP: Logged

Louis Bornwasser
Film God

Posts: 4441
From: prospect ky usa
Registered: Mar 2005


 - posted 06-14-2006 08:08 AM      Profile for Louis Bornwasser   Author's Homepage   Email Louis Bornwasser   Send New Private Message       Edit/Delete Post 
Given that there are more "falses" than real alarms and given that epileptic seizures are not that rare, it has occurred to me that the STROBE is a very bad thing. Louis

 |  IP: Logged

Dennis Benjamin
Phenomenal Film Handler

Posts: 1445
From: Denton, MD
Registered: Feb 2002


 - posted 06-14-2006 08:24 AM      Profile for Dennis Benjamin   Author's Homepage   Email Dennis Benjamin   Send New Private Message       Edit/Delete Post 
The city of Las Vegas has the right idea:

No pull alarms!

They do have extremely strict fire alarm codes, due to the MGM fire back in the day. I think I have had an idiot teenager pull an alarm at every other theatre that I have worked at - except in Vegas! However, Las Vegas is where I had an actual theatre fire. A six year old child got a hold of some matches (from a local casino) that he had found on the ground. He had auditorium #8 lit up like a Christmas Tree. Lesson I learned that day: While the cloth on the outside of a theatre chair is fireproof, once a match burns a hole through the material - the foam inside will put off 4 foot flames!

[eyes]

 |  IP: Logged

Mark Hajducki
Jedi Master Film Handler

Posts: 500
From: Edinburgh, UK
Registered: May 2003


 - posted 06-14-2006 08:48 AM      Profile for Mark Hajducki   Email Mark Hajducki   Send New Private Message       Edit/Delete Post 
quote: David Buckley
In the UK its common (but not universal) practice at live theatres to have the fire alarm system operate a few red lights in specific areas, so that the management and staff have a chance to evaluate if there really is a fire and if there isn't then to cancel the alarm. If not cancelled the system goes into full alarm after 30 secs or a minute usually. If two or more sensors trigger then a full alarm is immediately triggered.
Worked in a complex with that system, the main problem was if an alarm was triggered somewhere else in the building it could not always be reset in time. The site also ran a staged evacuation (screen by screen) to reduce loads on the escape stairs.

quote:
In the UK if you called the fire brigade out for a falsie there used to be heinous charges for wasting their time, but I don't know if that is still the case.
I think that is no longer the case (unless you have lots of call outs) since the advice given is to call the fire brigade if you suspect a fire. (automatic callouts are required for most large buildings)

quote: Louis Bornwasser
Given that there are more "falses" than real alarms and given that epileptic seizures are not that rare, it has occurred to me that the STROBE is a very bad thing.
The strobes used are the 'security' type that flash once or twice a second (like the lights on emergency vehicles), not a disco type strobe.

 |  IP: Logged

David L Parlier
Film Handler

Posts: 23
From: Franklin, NC, U.S.A.
Registered: Oct 2003


 - posted 06-14-2006 09:58 AM      Profile for David L Parlier   Author's Homepage   Email David L Parlier   Send New Private Message       Edit/Delete Post 
quote:
Jack Ondracek wrote: When the fire marshal inspected my indoor theatre, he specifically authorized a system whereby all public pull stations would show at an annunciator station in the concessions area.
This sounds very similar to the system that we had installed at my theater and indeed it is convenient. However, there are some major problems with this type of system and I would suggest you go back and read the Fire Marshal's wordage. I recently went back and reviewed our fire procedure policy because I questioned this type of system for safety reasons. What I found was that the now retired fire marshal authorized our current type of system but he wrote it up to completely 100% protect himself from liability. I am sure he knew this type of system was not ideal and or certainly not the safest for the general public but was the easiest for the owners of the theater.

Liability upon the general managers and or owners of theaters should be a major concern especially after the night club fire a while back. It should also be noted that in the state of NC and our county there are no "grandfather claus" when it comes to fire inspection. So, with my knowledge in the fire business and with the current fire inspector we have been working over the past year to get the theater up to current standards and to protect the owners for a future fire. Just something to consider!

 |  IP: Logged

Jack Ondracek
Film God

Posts: 2348
From: Port Orchard, WA, USA
Registered: Oct 2002


 - posted 06-14-2006 10:59 AM      Profile for Jack Ondracek   Author's Homepage   Email Jack Ondracek   Send New Private Message       Edit/Delete Post 
Good points, David.
This system was actually an upgrade from the one that was in the building before I got it. The previous system ONLY signalled in the lobby, and any call to the fire department had to be made manually... by phone!

I don't know that there's a universal "grandfather clause" here, either... but changes are usually required when a building has been closed for awhile... and major changes (sprinklers, etc) when repurposing a structure.

 |  IP: Logged

John-Layton Jenkins
Film Handler

Posts: 15
From: Carrollton, Tx, USA
Registered: Dec 2003


 - posted 06-14-2006 12:32 PM      Profile for John-Layton Jenkins   Email John-Layton Jenkins   Send New Private Message       Edit/Delete Post 
When I worked at the UA MacArthur back when we did the midnight showing of The Two Towers, someone pulled the alarm twice that night, but both times before the shows started. The first time, some people got up and wandered around. The 2nd time, not one person moved. I went out to the lobby and there were maybe 4-10 people asking what was going on. We had 3 sold out screens, roughly 1400 people, and they were ready to burn to death to watch that movie.

 |  IP: Logged



All times are Central (GMT -6:00)
This topic comprises 2 pages: 1  2 
 
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.