Curious if anyone has dealt with this before. I think I have a fault somewhere in my 3 phase service.
I have a 23B at the drive in connected to two hot legs of my 3 phase. Worked fine for 9 years. However… It just started not lighting the bulb when one of the other projectors wasn’t on, which never happened before. I read the diag package and the lamp power supply log is saying a limit was reached and the voltage was 277.4 v. When I read back before this problem when everything worked fine, the voltage was 240.2. I took a reading of my 3 phase each leg to ground in the panel and got 138v 154v and 129v. Each leg of this 3 phase to ground should be approximately 120 ish to ground.
Im thinking I might need to call the power company. Anyone experience this before?
I have a 23B at the drive in connected to two hot legs of my 3 phase. Worked fine for 9 years. However… It just started not lighting the bulb when one of the other projectors wasn’t on, which never happened before. I read the diag package and the lamp power supply log is saying a limit was reached and the voltage was 277.4 v. When I read back before this problem when everything worked fine, the voltage was 240.2. I took a reading of my 3 phase each leg to ground in the panel and got 138v 154v and 129v. Each leg of this 3 phase to ground should be approximately 120 ish to ground.
Im thinking I might need to call the power company. Anyone experience this before?